Welly's Boiler woes

Post by Welly »

Got home from Work last Friday night to the not uncommon 'Boiler Lockout' on our 11 year old Potterton Promax Condensing Boiler. No problem, I'll press reset and it'll re-start......no it won't.

I'm a HVAC engineer (without Gas Certification, I don't 'work on' boilers, I manage projects) but am knowledgeable enough after 25 years to find my way around a Domestic boiler and narrow-down faults. Anyhoo the boiler was trying to start; I had the fan running, pilot gas, but no spark being generated....then lock out (ignition failed, no flame sensed, back to square one).

Goes back to the yard to pick up 3 x electric heaters, switch on the immersion heater for Hot Water, and ponder the problem. Had a squint at the Ignition PCB and it looked like it'd run hot in a couple of places (failed components) but I re-soldered a previous fix on the board anyway......still no joy.

Saturday I order a reconditioned PCB for £30.00 + post + refundable deposit (when I return my old one).....being Saturday it'll get processed on Monday, I'll see it on Tuesday, the house is now down to 15 deg - this doesn't sound too bad but that's cold for the Missus......Sunday passes.....Kids start complaining......Monday comes.....complaints coming in thick and fast.....all eyes are on me! will this amateur* diagnosis be right? what if it's not? ....all eyes are on me.....Tuesday comes.....the day of reckoning.....the PCB arrives at my work...the suspense is tremendous.....I dart home in the afternoon to fit the thing....the house is cold and no-one's home.....gingerly I offer the PCB to the boiler (like presenting a gift)....please work.....please f*cking work.....connect the multi-plug and the "HT" lead.....

Carried out some checks* ......I'm ready......trembling I power up and 'call' for heat..........Fan runs.......Pilot Gas enabled.....Tick Tick of the ignition......Whoomph.....a FLAME......full Gas......Woo Hoo! Boiler running spot on 8)

4 hours it took for the house to reach 19 deg, then later 21 as a 'treat' :cheesy:

I tell you though, I was shitting myself if that fix didn't work it would've been a new Boiler, more delays, and the weather's turning even more cold. In case you wondered, I don't have any Boiler Care packages, the reason being that I kinda work in that industry anyway and the Potterton is a twat to work on - many engineers won't touch them, if you open the combustion chamber cover you SHOULD replace all the seals @ £150.00 the whole thing is a piece of sh*t so you keep it running as best you can. It's being binned this Summer anyway.
Cars in my care:
2021 Kia Spottage 1.6 Pez Turbo Dual Clutch Gearbox Trickery
2013 Renner Twingo - donkey work
User avatar
steve_earwig
Moderator
Posts: 19813
Joined: Thu Oct 04, 2007 6:09 pm
Location: Jastrebarsko, Croatia http://www.jastrebarsko.hr/lokacija/

Re: Welly's Boiler woes

Post by steve_earwig »

Why replace it, should be good for another 11 years now :wink:

Is there much else to go wrong on it? What I'd worry about is buying something even less reliable, from Sam's thread they're just as unreliable as all other household stuff, just enough to get them out of guarantee and *pop*, time to buy another one :roll:

Pilot light?
Image
We don't need no stinking pilot light :twisted:
Unskilled meddling sin©e 2007

The submitted form was invalid. Try submitting again.
User avatar
Welly
The moderator formally known as Welton
Posts: 15033
Joined: Tue Jan 10, 2006 12:52 pm
Location: East Midlandfordshire

Re: Welly's Boiler woes

Post by Welly »

The boiler is on its last legs, probably past it, like you say it's an 'appliance' modern fancy Boilers last about 8 to 10 years and become uneconomical to repair.

On mine the main burner is a fragile fabric/ceramic thing (£200.00) and is wayyy past its best (and will need those new seals I mentioned just to get to the thing) and the Aluminium heat exchanger (££££) is corroded (by the condensed water) so it's killing itself. A good condensing boiler will have a stainless steel heat exchanger, oh but they can crack.....

I could spend about £600.00 on the thing but a brand new Glow Worm is £650.00 and a much better investment.
Cars in my care:
2021 Kia Spottage 1.6 Pez Turbo Dual Clutch Gearbox Trickery
2013 Renner Twingo - donkey work
User avatar
Bailes1992
Moderator
Posts: 4292
Joined: Mon Dec 24, 2007 4:13 pm
Location: Bridgend, South Wales

Re: Welly's Boiler woes

Post by Bailes1992 »

The other half has a Potterton Powermax boiler. It has it's hot water tank built into the boiler. Which as a result means when it goes wrong there isn't an immersion to switch on.
And Like you say when it goes wrong there is nobody who is willing to work on it!

The house I've just bought I thought there was a combi but apparently not. There's 15 year old boiler with a hot water tank. I'm kind of relieved about it. I can get a thicker jacket fitted to the hot water tank and an immersion heater. At least then if it goes wrong I can flick the immersion on!
2020 BMW 520d MSport Touring My Daily
2017 Dacia Logan MCV 1.5DCi Laureate Wifes
1996 Land Rover Defender 90 County SW 300TDi My Toy
2003 Ford Mondeo ST220 3.0 V6 My Other Toy
teamster1975
Site Admin & Mad Biker!
Posts: 6277
Joined: Sun Oct 28, 2007 8:07 pm
Location: Woking, Surrey

Re: Welly's Boiler woes

Post by teamster1975 »

Good result Welly!
We had a Wickes boiler at our last place and I had to replace the diaphragm in the DHW flow switch and the microswitch that triggered the CH. Very satisfying when you can fix them yourself! (No I would never touch the gas side :supafrisk: )
1996 406 1.8LX Got a bad case of hydro lock!
1996 406 Executive 2.0 Turbo XU10J2TE No longer hangin' on in there :(
1997 Honda CB500V
2003 Volvo V40 1.8 GDi SE killed by a nutter in a beemer 5 series
2008 Mondeo 2.0 TDCi Titanium X

"Always look on the bright side of life, dedo, dedo dedodedo"
User avatar
Welly
The moderator formally known as Welton
Posts: 15033
Joined: Tue Jan 10, 2006 12:52 pm
Location: East Midlandfordshire

Re: Welly's Boiler woes

Post by Welly »

Simple heating systems are definitely best IMO, I've got a Hot Water Cylinder heated by the Boiler or an Immersion and with a huge storage tank in the loft, we run 2 x power showers together and never run out of hot water. The Heating boiler is open vented with a Feed & Expansion tank in the loft, again as simple as possible.

Bailes - were you thinking of adding an Immersion heater to your cylinder? I tried doing that at my last 1960's house and split the copper cylinder :shock: it kinda folded in on itself when I was trying to unscrew the blanking plug [think: foot up against the wall and using full force] then everyone at work told me I shoulda heated the freds first and left the cylinder full of water to stabilise the shape of the copper vessel - at least just to crack open the plug, and then drain it down.
Cars in my care:
2021 Kia Spottage 1.6 Pez Turbo Dual Clutch Gearbox Trickery
2013 Renner Twingo - donkey work
User avatar
Doggy
Mod with a 2.2 HDi, De-Fapped!
Posts: 10710
Joined: Mon Oct 13, 2008 11:49 pm
Location: Northants

Re: Welly's Boiler woes

Post by Doggy »

Welly wrote:Simple heating systems are definitely best IMO, I've got a Hot Water Cylinder heated by the Boiler or an Immersion and with a huge storage tank in the loft, we run 2 x power showers together and never run out of hot water. The Heating boiler is open vented with a Feed & Expansion tank in the loft, again as simple as possible.
I'm more or less with you there, 'cept I've got a non-condensing balanced flue boiler, (It was 2 years old, but had never been installed - £29 on eBay). :cheesy:
which I picked up the year after condensing boilers became effectively mandatory, so we 'installed' it the previous year. :supafrisk:

I also have an inset multifuel boiler stove which runs almost exclusively on FOC waste wood. (So far this winter I've had to buy 2 bags of coal). We heat the house using the gas boiler/timeclock for the mornings and then run everything from afternoon till bedtime using the stove.

(In case your wondering, the stove circulates round the indirect coil in the HW tank by gravity, the gas boiler heats the water via an 'immersion blade' - water/water heat exchanger that screws in like an immersion heater. We had to solder in a second boss for the electric immersion heater.)

Well done sorting out the boiler. My one needed a gas valve about 5 years ago, then a year or two ago refused to light cause the HT cable to the ignition electrode was tracking to earth. Bit of high temp sleeving sorted that.

Gives you a nice, warm feeling. :D
2002 HDi 2.2 Exec Estate, (2008-12) (wonderful)
2003 HDi 2.2 6-speed Exec Estate (2012-19) (also a gem)
2009 Citroen C5 2.0 HDi VTR+ Estate (godawful heap)
2008 BMW E91 330i touring (great fun - murdered by a reversing SUV)
2007 BMW E91 325i touring (slower smoother quieter)
User avatar
DaiRees
Site Admin
Posts: 5377
Joined: Sat Aug 06, 2005 8:24 am
Location: Merthyr Tydfil, South Wales (God's Country!)

Re: Welly's Boiler woes

Post by DaiRees »

Doggy wrote:Gives you a nice, warm feeling. :D
Haha, I see what you did there Doggy! :cheesy:

We've got a 17 year old Vaillant combi. Had a few issues over the years but generally it's been great. Saying no more on the subject, fate, tempting, etc....
Image
Playtime_Fontayne wrote:"Dai Rees Supplier of Fine Automobilia. Established 2007"
User avatar
Bailes1992
Moderator
Posts: 4292
Joined: Mon Dec 24, 2007 4:13 pm
Location: Bridgend, South Wales

Re: Welly's Boiler woes

Post by Bailes1992 »

Welly wrote:Simple heating systems are definitely best IMO, I've got a Hot Water Cylinder heated by the Boiler or an Immersion and with a huge storage tank in the loft, we run 2 x power showers together and never run out of hot water. The Heating boiler is open vented with a Feed & Expansion tank in the loft, again as simple as possible.

Bailes - were you thinking of adding an Immersion heater to your cylinder? I tried doing that at my last 1960's house and split the copper cylinder :shock: it kinda folded in on itself when I was trying to unscrew the blanking plug [think: foot up against the wall and using full force] then everyone at work told me I shoulda heated the freds first and left the cylinder full of water to stabilise the shape of the copper vessel - at least just to crack open the plug, and then drain it down.
What do you mean by a hot water tank and then a storage tank? I thought you just had one hot water tank that boiler heats and a tank above with a float that feeds the hot water tank?

I was planning on fitting a cold water tank in the attic to feed the electric shower, that way if anyone switches a tap on I won't be boiled to death like I am in my current house. :roll:

I don't want to touch my hot water tank, I only do 'lectrics. 'Lectrics are much safer ya' know! People have died in water. Therefore I was planning to get you down for free to fit my immersion heater? I knew you were a jolly good chap with an economical car who earns plenty of money so you wouldn't mind. :cheesy:
Doggy wrote:
I also have an inset multifuel boiler stove which runs almost exclusively on FOC waste wood. (So far this winter I've had to buy 2 bags of coal). We heat the house using the gas boiler/timeclock for the mornings and then run everything from afternoon till bedtime using the stove.

(In case your wondering, the stove circulates round the indirect coil in the HW tank by gravity, the gas boiler heats the water via an 'immersion blade' - water/water heat exchanger that screws in like an immersion heater. We had to solder in a second boss for the electric immersion heater.)
Would love a setup like this. How well does the gravity fed system work?
Saying that, the house I've just bought doesn't have a chimney! :?
2020 BMW 520d MSport Touring My Daily
2017 Dacia Logan MCV 1.5DCi Laureate Wifes
1996 Land Rover Defender 90 County SW 300TDi My Toy
2003 Ford Mondeo ST220 3.0 V6 My Other Toy
User avatar
Welly
The moderator formally known as Welton
Posts: 15033
Joined: Tue Jan 10, 2006 12:52 pm
Location: East Midlandfordshire

Re: Welly's Boiler woes

Post by Welly »

Vaillant are the best, the end. Well apart from maybe Viessmann (££££).

Worcester-Bosch aren't as good as they used to be (according to service people) whereas Glow Worm are regarded well, easy to work on and parts are cheap.

Bailes - I meant the Hot Water Cylinder has a Feed & Expansion Tank up in the loft, the Showers take their Cold water straight from the Tank so cannot be affected by toilet-flushing or sink tap opening etc. And I am fully booked until 2036, sorry :)
Cars in my care:
2021 Kia Spottage 1.6 Pez Turbo Dual Clutch Gearbox Trickery
2013 Renner Twingo - donkey work
trufflehunt
3.0 24v
Posts: 552
Joined: Sat Aug 25, 2012 9:15 pm
Location: Axbridge, Somerset

Re: Welly's Boiler woes

Post by trufflehunt »

My sister and brother-in-law live on a Scottish island, Arran. Last winter, with the storms and snow,
all the power was out for ages, and they discovered just how cold a house could be.

The instant the ferries were back on, they were off to the mainland for a hefty stove.
2006 Toyota Yaris 1.0 T3
1993 Mazda MX5 Mk1 1.6
2000 "W" HDI 110 Executive Saloon (Recycled).
User avatar
steve_earwig
Moderator
Posts: 19813
Joined: Thu Oct 04, 2007 6:09 pm
Location: Jastrebarsko, Croatia http://www.jastrebarsko.hr/lokacija/

Re: Welly's Boiler woes

Post by steve_earwig »

Welly wrote:Bailes - I meant the Hot Water Cylinder has a Feed & Expansion Tank up in the loft, the Showers take their Cold water straight from the Tank so cannot be affected by toilet-flushing or sink tap opening etc. And I am fully booked until 2036, sorry :)
Storage tank, cold water tank, tank with a float, expansion tank - it's a header tank :frown: I think if Sam just puts one in his loft he'll be a bit disappointed with the flow rate from the shower, unless he uses a power shower like what you does Welly. But then he'll have to make sure it's a) big enough to supply all the water he needs and b) not so big it ends up crashing through the ceiling...

The Croats don't believe in header tanks, heating is pressurised with a point next to the boiler to either drain it or put more pressure in the system, the hot water is mains fed as is the cold throughout the house, so no nasty things floating about in the header tank in the loft and bathroom water is always safe to drink (unless something nasty has got into it from the spring again...)

Incidentally, a few years back I got some thermostatickaly controlled shower mixer taps here, the one at my gaff works great but the one in my wife's house here long since went in the bin. Problem is the mains here is at about 6 bar :shock: (it's a long time since I looked but something like that anyway, enough to have the hose pipe do a dance and make holes in the ground) so it has a pressure regulator on it. Up at my house, which is further out of town, the pressure is tolerable without a regulator, but here it would be unacceptable to try and fill a glass of water and get soaked every time. I was trying to explain this to the plumber here, the regulator is basically a valve with a spring on it, once the pressure on the house side of the valve reaches the setting the valve shuts against the spring and only opens once the pressure drops again. What it doesn't take into account is the 80 litres in the electric HWT and the 90 in the wood burner. When water gets hot it expands, as the system is sealed by the regulator the extra pressure end stops the gauge at 10+ bar. It killed 3 of these shower mixers before I worked it out, the temperature is regulated by a bi-metal coil spring which is open to mains all the time and the cataclysmic water pressure was effectively crushing them to oblivion. He wouldn't have it though, even when I showed him pictures of the pressure meter on the regulator end-stopped :roll: What I'm actually meant to do is fit vents here and there, apparently it's quite acceptable to have them dripping all over the place :evil:
Unskilled meddling sin©e 2007

The submitted form was invalid. Try submitting again.
User avatar
lozz
3.0 24v
Posts: 11908
Joined: Thu Oct 07, 2010 10:18 pm
Location: where-ever

Re: Welly's Boiler woes

Post by lozz »

Potterton are a night mare,

There is a chap thats made a CD full of info on how to repair these and save money' (ebay iirc)
Most engineers will repair them,as theyve got a direct number to potterton,

Best thing to do with these is buy spare parts to put away ..good boilers but unrelible,ours never broke down in summer always winter, :(
User avatar
Bailes1992
Moderator
Posts: 4292
Joined: Mon Dec 24, 2007 4:13 pm
Location: Bridgend, South Wales

Re: Welly's Boiler woes

Post by Bailes1992 »

I don't fancy a power shower on an old fashioned boiler because of the cost to run it and inefficiency etc.

But I don't fancy a power shower on a combi either because if the boiler packs up you don't have a shower :roll:
2020 BMW 520d MSport Touring My Daily
2017 Dacia Logan MCV 1.5DCi Laureate Wifes
1996 Land Rover Defender 90 County SW 300TDi My Toy
2003 Ford Mondeo ST220 3.0 V6 My Other Toy
User avatar
Welly
The moderator formally known as Welton
Posts: 15033
Joined: Tue Jan 10, 2006 12:52 pm
Location: East Midlandfordshire

Re: Welly's Boiler woes

Post by Welly »

Wiggy - don't you have any expansion vessels to take up the expanded warty pressure?

Bailes - you can't fit a Power Shower to a Combi Boiler, the shower pump will try to drag water through the Combi at a rate of knots and the boiler won't keep up, and the water pressure will also be too high (feeding the shower pump). Power Showers are designed to draw water from a storage vessel at equal-ish pressures, I have the showers with a built-in pump (look like an electric wall mounted shower) and they are very good, if a tad noisy, but they do need tank-fed Cold and via the Tank fed Hot.